SPECULATION: Could temporally transient and spatially isolated magnetic field fluctuations be causing the transformer failures?

 
Anonymous Coward
User ID: 1382372
India
05/15/2011 04:55 PM
Report Abusive Post
Report Copyright Violation
SPECULATION: Could temporally transient and spatially isolated magnetic field fluctuations be causing the transformer failures?
Transformer Failure Modes

The following failure scenarios are given by the International Association of Inspection Engineers, [link to www.bplglobal.net] (listed in order of frequency). I've also included my own thoughts on the probability that each failure mode might explain the recent string of failures (in italics).

Insulation failure

Insulation failures were the leading cause of failure in this study. This category excludes those failures where there was evidence of a lightning or a line surge. There are actually four factors that are responsible for insulation deterioration: pyrolosis (heat), oxidation, acidity, and moisture. But moisture is reported separately. The average age of the transformers that failed due to insulation was 18 years.

This failure mode would require all of the transformers that have blown to have the same degree of insulation deterioration at nearly the same time. This seems highly unlikely unless they all overheated - but that would imply that the feed voltage to all of these transformers was higher than the design voltage. This might be somewhat reasonable if there were a computer virus affecting power plant outputs. The other possibility is solar activity. However, solar data shows that the sun, although quite active, is not spitting out anything extreme in terms of coronal mass ejections.

Design/Manufacturing failure

This category includes conditions such as: loose or
unsupported leads, loose blocking, poor brazing, inadequate core insulation, inferior short circuit
strength, and foreign objects left in the tank. In this study, this is the second leading cause of
transformer failures.

This failure mode appears to be highly unlikely although it would be interesting to know the make/model of all these transformers that have failed and when they were installed.

Oil contamination failure

This category pertains to those cases where oil contamination can be established as the cause of the failure. This includes sludging and carbon tracking.

This failure mode also appears to be highly unlikely.

Overloading

This category pertains to those cases where actual overloading could be established as the cause of the failure. It includes only those transformers that experienced a sustained load that exceeded the nameplate capacity.

This goes along with insulation failure - not likely but possible.

Fire/explosion

This category pertains to those cases where a fire or explosion outside the transformer can be established as the cause of the failure. This does not include internal failures that resulted in a fire or explosion.

Obviously not the case.

Line surge

This category includes switching surges, voltage spikes, line faults/flashovers, and other T&D abnormalities. This significant portion of transformer failures suggests that more attention should be given to surge protection, or the adequacy of coil clamping and short circuit strength.

Again, very similar to insulation failure and overloading.

Maintenance/operation

Inadequate or improper maintenance and operation was a major
cause of transformer failures, when you include overloading, loose connections and moisture. This category includes disconnected or improperly set controls, loss of coolant, accumulation of dirt & oil, and corrosion. Inadequate maintenance has to bear the blame for not discovering
incipient troubles when there was ample time to correct it.

Not a likely failure mode.

Floods

The flood category includes failures caused by inundation of the transformer due to man-made or natural caused floods. It also includes mudslides.

Obviously not the case here.

Loose connections

This category includes workmanship and maintenance in making
electrical connections. One problem is the improper mating of dissimilar metals, although this has decreased somewhat in recent years. Another problem is improper torquing of bolted connections. Loose connections could be included in the maintenance category, but we customarily report it separately.

Not a likely failure mode.

Lightning

Lightning surges are considerably fewer in number than previous studies we have published. Unless there is confirmation of a lightning strike, a surge type failure is categorized as “Line Surge”.

There was a storm in the Ft. Worth area when the transformers failed. I don't think this was the case for the Wisconsin and Las Vegas explosions. Someone correct me if I am wrong. However, even with the Ft. Worth explosions it wasn't a single isolated explosion as one would expect with a lightning strike.

Moisture

The moisture category includes failures caused by leaky pipes, leaking roofs, water entering the tanks through leaking bushings or fittings, and confirmed presence of moisture in the insulating oil. Moisture could be included in the inadequate maintenance or the insulation failure
category above, but we customarily report it separately.

Not a likely failure mode.

Speculation

I do not believe these transformer failures are caused by solar activity (at least, not any type of activity that we routinely measure). This pretty much leaves insulation failure or overload as the only failure mode above that makes any sense. Given the number of failures we have observed over the last few days, the only explanation that seems appropriate is that the power output and distribution controls have been compromised by a computer virus.

However, there is another possible explanation in my mind but it is far more speculative than anything else presented here. The heart of a transformer is the iron core which has a high magnetic permeability and uses the magnetic flux generated by the high voltage windings to induce a low voltage in the other set of windings. If there were spatially isolated and temporally transient fluctuations occurring in the geomagnetic field (or some extraterrestrial magnetic field) transformers would be the first place this would be expected to manifest itself. The iron cores have such a high magnetic permeability that the field generated within the volume of the core could be drastically changed by magnetic fields of relatively modest strength. The variation of the magnetic field within the core would influence the input and output voltages in the transformer. If the effect were large enough you might see overloading of the transformer which would cause it to fail.

I have no idea if this hypothesis is reasonable. Even if it is correct, I don't know what would be causing magnetic field fluctuations to occur in a way that is spatially isolated and temporally transient. Yet, it is still thought-provoking. There is certainly SOMETHING causing these failures. The question is what? It is beyond our normal everyday experience to observe this kind of phenomenon.
Anonymous Coward
User ID: 1379771
United States
05/15/2011 04:59 PM
Report Abusive Post
Report Copyright Violation
Re: SPECULATION: Could temporally transient and spatially isolated magnetic field fluctuations be causing the transformer failures?
The heart of a transformer is the iron core which has a high magnetic permeability and uses the magnetic flux generated by the high voltage windings to induce a low voltage in the other set of windings. If there were spatially isolated and temporally transient fluctuations occurring in the geomagnetic field (or some extraterrestrial magnetic field) transformers would be the first place this would be expected to manifest itself. The iron cores have such a high magnetic permeability that the field generated within the volume of the core could be drastically changed by magnetic fields of relatively modest strength. The variation of the magnetic field within the core would influence the input and output voltages in the transformer. If the effect were large enough you might see overloading of the transformer which would cause it to fail.
 Quoting: Anonymous Coward 1382372


This.
Life and Love

User ID: 1324426
United States
05/15/2011 05:04 PM
Report Abusive Post
Report Copyright Violation
Re: SPECULATION: Could temporally transient and spatially isolated magnetic field fluctuations be causing the transformer failures?
The heart of a transformer is the iron core which has a high magnetic permeability and uses the magnetic flux generated by the high voltage windings to induce a low voltage in the other set of windings. If there were spatially isolated and temporally transient fluctuations occurring in the geomagnetic field (or some extraterrestrial magnetic field) transformers would be the first place this would be expected to manifest itself. The iron cores have such a high magnetic permeability that the field generated within the volume of the core could be drastically changed by magnetic fields of relatively modest strength. The variation of the magnetic field within the core would influence the input and output voltages in the transformer. If the effect were large enough you might see overloading of the transformer which would cause it to fail.
 Quoting: Anonymous Coward 1382372


This.
 Quoting: Anonymous Coward 1379771


Errr.... no.

A transformer is designed to contain the magnetic fields, else it would be highly inefficient. While a current applied to one of the transformer's windings can be amplified, the total power cannot. Moreover, and external (to the transformer) magnetic field would have little effect on what's happening in the transformer iself.
We become like that to which we are devoted. - Choose wisely.
scrimmy

User ID: 1384877
United States
05/15/2011 05:04 PM
Report Abusive Post
Report Copyright Violation
Re: SPECULATION: Could temporally transient and spatially isolated magnetic field fluctuations be causing the transformer failures?
i live in Fl. , lastnight i witnessed several transformers glowing at around 9pm. me and my family did not hear any explosions.

Last Edited by scrimmy on 05/15/2011 05:05 PM
Anonymous Coward
User ID: 1379771
United States
05/15/2011 05:06 PM
Report Abusive Post
Report Copyright Violation
Re: SPECULATION: Could temporally transient and spatially isolated magnetic field fluctuations be causing the transformer failures?
The heart of a transformer is the iron core which has a high magnetic permeability and uses the magnetic flux generated by the high voltage windings to induce a low voltage in the other set of windings. If there were spatially isolated and temporally transient fluctuations occurring in the geomagnetic field (or some extraterrestrial magnetic field) transformers would be the first place this would be expected to manifest itself. The iron cores have such a high magnetic permeability that the field generated within the volume of the core could be drastically changed by magnetic fields of relatively modest strength. The variation of the magnetic field within the core would influence the input and output voltages in the transformer. If the effect were large enough you might see overloading of the transformer which would cause it to fail.
 Quoting: Anonymous Coward 1382372


This.
 Quoting: Anonymous Coward 1379771


Errr.... no.

A transformer is designed to contain the magnetic fields, else it would be highly inefficient. While a current applied to one of the transformer's windings can be amplified, the total power cannot. Moreover, and external (to the transformer) magnetic field would have little effect on what's happening in the transformer iself.
 Quoting: Life and Love


Oh. Okay. I am now a little more educated on the subject.

Do you have any ideas to explain these extraordinary failures?
Anonymous Coward (OP)
User ID: 1382372
India
05/15/2011 05:09 PM
Report Abusive Post
Report Copyright Violation
Re: SPECULATION: Could temporally transient and spatially isolated magnetic field fluctuations be causing the transformer failures?
The heart of a transformer is the iron core which has a high magnetic permeability and uses the magnetic flux generated by the high voltage windings to induce a low voltage in the other set of windings. If there were spatially isolated and temporally transient fluctuations occurring in the geomagnetic field (or some extraterrestrial magnetic field) transformers would be the first place this would be expected to manifest itself. The iron cores have such a high magnetic permeability that the field generated within the volume of the core could be drastically changed by magnetic fields of relatively modest strength. The variation of the magnetic field within the core would influence the input and output voltages in the transformer. If the effect were large enough you might see overloading of the transformer which would cause it to fail.
 Quoting: Anonymous Coward 1382372


This.
 Quoting: Anonymous Coward 1379771


Errr.... no.

A transformer is designed to contain the magnetic fields, else it would be highly inefficient. While a current applied to one of the transformer's windings can be amplified, the total power cannot. Moreover, and external (to the transformer) magnetic field would have little effect on what's happening in the transformer iself.
 Quoting: Life and Love


This is utter trash. The entire reason a transformer works is that the magnetic field applied by the high voltage windings, H, is amplified inside the iron core producing a field of strength B.

B = uH where u is the magnetic permeability of the iron core

Any magnetic field whatsoever that encounters the iron core will follow this same equation, becoming amplified within the material itself.
Life and Love

User ID: 1324426
United States
05/15/2011 05:14 PM
Report Abusive Post
Report Copyright Violation
Re: SPECULATION: Could temporally transient and spatially isolated magnetic field fluctuations be causing the transformer failures?
The heart of a transformer is the iron core which has a high magnetic permeability and uses the magnetic flux generated by the high voltage windings to induce a low voltage in the other set of windings. If there were spatially isolated and temporally transient fluctuations occurring in the geomagnetic field (or some extraterrestrial magnetic field) transformers would be the first place this would be expected to manifest itself. The iron cores have such a high magnetic permeability that the field generated within the volume of the core could be drastically changed by magnetic fields of relatively modest strength. The variation of the magnetic field within the core would influence the input and output voltages in the transformer. If the effect were large enough you might see overloading of the transformer which would cause it to fail.
 Quoting: Anonymous Coward 1382372


This.
 Quoting: Anonymous Coward 1379771


Errr.... no.

A transformer is designed to contain the magnetic fields, else it would be highly inefficient. While a current applied to one of the transformer's windings can be amplified, the total power cannot. Moreover, and external (to the transformer) magnetic field would have little effect on what's happening in the transformer iself.
 Quoting: Life and Love


Oh. Okay. I am now a little more educated on the subject.

Do you have any ideas to explain these extraordinary failures?
 Quoting: Anonymous Coward 1379771


Electrical transmission isn't my specialty (electromagnetics is), but the first step would be to look at failure rates vs. time. Using the word "extraordinary" may not be justified.

In the last 10 years there have been two transformer failures in my neighborhood, both of which came on suddenly. I have no idea what is normal and what is not normal.

In the article you cited, it looks as if there were 20-25 failures per year during the years 1995-2001. The article predicts many more failures in the years to come due to the aging of the "transformer fleet." Apparently, that is happening.

Figure 6 in the article predicts that the number of failures in 2011 will be about 2.5x the number of failures in 1999, so the 20-25 failures per year in the 1995-2000 time period could translate into 40-50 (2x) or 50-62 (2.5x) today.
We become like that to which we are devoted. - Choose wisely.
Life and Love

User ID: 1324426
United States
05/15/2011 05:15 PM
Report Abusive Post
Report Copyright Violation
Re: SPECULATION: Could temporally transient and spatially isolated magnetic field fluctuations be causing the transformer failures?
The heart of a transformer is the iron core which has a high magnetic permeability and uses the magnetic flux generated by the high voltage windings to induce a low voltage in the other set of windings. If there were spatially isolated and temporally transient fluctuations occurring in the geomagnetic field (or some extraterrestrial magnetic field) transformers would be the first place this would be expected to manifest itself. The iron cores have such a high magnetic permeability that the field generated within the volume of the core could be drastically changed by magnetic fields of relatively modest strength. The variation of the magnetic field within the core would influence the input and output voltages in the transformer. If the effect were large enough you might see overloading of the transformer which would cause it to fail.
 Quoting: Anonymous Coward 1382372


This.
 Quoting: Anonymous Coward 1379771


Errr.... no.

A transformer is designed to contain the magnetic fields, else it would be highly inefficient. While a current applied to one of the transformer's windings can be amplified, the total power cannot. Moreover, and external (to the transformer) magnetic field would have little effect on what's happening in the transformer iself.
 Quoting: Life and Love


This is utter trash. The entire reason a transformer works is that the magnetic field applied by the high voltage windings, H, is amplified inside the iron core producing a field of strength B.

B = uH where u is the magnetic permeability of the iron core

Any magnetic field whatsoever that encounters the iron core will follow this same equation, becoming amplified within the material itself.
 Quoting: Anonymous Coward 1382372


OP leaves out a lot of stuff, so his conclusions are faulty. Perhaps I should return my PhD in Electromagnetic Theory, forget my 35 years of experience, and sell mymulti-million dollar business in EM consulting.
We become like that to which we are devoted. - Choose wisely.
Anonymous Coward (OP)
User ID: 1382372
India
05/15/2011 05:20 PM
Report Abusive Post
Report Copyright Violation
Re: SPECULATION: Could temporally transient and spatially isolated magnetic field fluctuations be causing the transformer failures?
...


This.
 Quoting: Anonymous Coward 1379771


Errr.... no.

A transformer is designed to contain the magnetic fields, else it would be highly inefficient. While a current applied to one of the transformer's windings can be amplified, the total power cannot. Moreover, and external (to the transformer) magnetic field would have little effect on what's happening in the transformer iself.
 Quoting: Life and Love


This is utter trash. The entire reason a transformer works is that the magnetic field applied by the high voltage windings, H, is amplified inside the iron core producing a field of strength B.

B = uH where u is the magnetic permeability of the iron core

Any magnetic field whatsoever that encounters the iron core will follow this same equation, becoming amplified within the material itself.
 Quoting: Anonymous Coward 1382372


OP leaves out a lot of stuff, so his conclusions are faulty. Perhaps I should return my PhD in Electromagnetic Theory, forget my 35 years of experience, and sell mymulti-million dollar business in EM consulting.
 Quoting: Life and Love


Please explain how I am in wrong in saying that an iron core placed in a magnetic field will produce a field inside that iron core proportional to the applied field?
Life and Love

User ID: 1324426
United States
05/15/2011 05:30 PM
Report Abusive Post
Report Copyright Violation
Re: SPECULATION: Could temporally transient and spatially isolated magnetic field fluctuations be causing the transformer failures?
Please explain how I am in wrong in saying that an iron core placed in a magnetic field will produce a field inside that iron core proportional to the applied field?
 Quoting: Anonymous Coward 1382372


I shall be happy to.

1. The reason that a transformer works is due to magnetic flux. A current flows in one winding and thereby creates a magnetic flux whose field line orientation is perpendicular to the winding. A second winding intercepts that flux, which induces a current into that second winding. The ratio of current in to current out is related to the ratio of the number of turns in each winding.

2. The reason that a transformer is efficient is that a permeable material is inserted where the flux lines couple between the windings. This confines the majority of the magnetic flux to the interior of the material, so that the amount that gets coupled to the second winding is maximized.

3. The permeable material in electrical transmission transformers is made up of insulated laminates (to reduce what are called 'eddy currents' - another form of loss an inefficiency) and are shaped in a closed path to keep the magnetic flux confined.

4. Since a transformer is a passive device, if the windings are such that the voltage is stepped up, e.g., 10:1, then the corresponding currents are steeped down, e.g., 1:10.

5. The same mechanism that confines the transformer's own magnetic flux (highly permeable material) also makes it extremely difficult for an external magnetic field to couple into the transformer windings in the same way.

6. An external field is much more likely to couple into the transmission line itself, e.g., from a CME or EMP event, and that externally generated current could overload a transformer, break down dielectrics, etc.

7. And yes, B = uH, but H = B/u, too. From outside the transformer it's basically a wash.

Hope this helps. hf

(That pblgobal article isn't a bad one... seems to be an advocacy piece for gov'ts to buy replacement transformers and have them installed.)
We become like that to which we are devoted. - Choose wisely.
Anonymous Coward
User ID: 1384912
United States
05/15/2011 05:32 PM
Report Abusive Post
Report Copyright Violation
Re: SPECULATION: Could temporally transient and spatially isolated magnetic field fluctuations be causing the transformer failures?
no
Anonymous Coward
User ID: 1379771
United States
05/15/2011 05:57 PM
Report Abusive Post
Report Copyright Violation
Re: SPECULATION: Could temporally transient and spatially isolated magnetic field fluctuations be causing the transformer failures?
The poster Love and Life has just poured cold common sense all over my fringe fantasies. Thanks for that, I guess.

I mean that, sincerely. Thank you. It is fun to imagine sci-fi reasons for why things change, but I also very much appreciate explanations from the real world.

What are you doing on this forum, anyway? Are you on some kind of mission to straighten out the lunatics?

Did you have any explanation for Trinity's little anomaly?:

[link to www.godlikeproductions.com]

What is your take on the popularity of the "electric universe"? Plasma physics?
Anonymous Coward (OP)
User ID: 1382372
India
05/15/2011 06:42 PM
Report Abusive Post
Report Copyright Violation
Re: SPECULATION: Could temporally transient and spatially isolated magnetic field fluctuations be causing the transformer failures?
Please explain how I am in wrong in saying that an iron core placed in a magnetic field will produce a field inside that iron core proportional to the applied field?
 Quoting: Anonymous Coward 1382372


I shall be happy to.

1. The reason that a transformer works is due to magnetic flux. A current flows in one winding and thereby creates a magnetic flux whose field line orientation is perpendicular to the winding. A second winding intercepts that flux, which induces a current into that second winding. The ratio of current in to current out is related to the ratio of the number of turns in each winding.

2. The reason that a transformer is efficient is that a permeable material is inserted where the flux lines couple between the windings. This confines the majority of the magnetic flux to the interior of the material, so that the amount that gets coupled to the second winding is maximized.

3. The permeable material in electrical transmission transformers is made up of insulated laminates (to reduce what are called 'eddy currents' - another form of loss an inefficiency) and are shaped in a closed path to keep the magnetic flux confined.

4. Since a transformer is a passive device, if the windings are such that the voltage is stepped up, e.g., 10:1, then the corresponding currents are steeped down, e.g., 1:10.

5. The same mechanism that confines the transformer's own magnetic flux (highly permeable material) also makes it extremely difficult for an external magnetic field to couple into the transformer windings in the same way.

6. An external field is much more likely to couple into the transmission line itself, e.g., from a CME or EMP event, and that externally generated current could overload a transformer, break down dielectrics, etc.

7. And yes, B = uH, but H = B/u, too. From outside the transformer it's basically a wash.

Hope this helps. hf

(That pblgobal article isn't a bad one... seems to be an advocacy piece for gov'ts to buy replacement transformers and have them installed.)
 Quoting: Life and Love


You obviously have more knowledge of transformers than I do...however, I would just like to point out that external magnetic fields can and do have real effects on transformers.

Please see:

[link to spie.org]
"Simulation of voltage transformer operation in the external magnetic fields (Proceedings Paper)"

This does not in any way validate the hypothesis I presented. But it seems at least conceivable to me that it might be a possibility.

Thanks for your insight.
Anonymous Coward
User ID: 1383040
United States
05/15/2011 06:58 PM
Report Abusive Post
Report Copyright Violation
Re: SPECULATION: Could temporally transient and spatially isolated magnetic field fluctuations be causing the transformer failures?
Yes, it has happened before, but never at a point when we have so many power lines etc... last time was 130 or so years ago. Telegraphs lines were shocking people, even when not plugged in. Google it, you'll see...
There have been plenty of times since we have the gird, that they have gone down due to solar flairs...
hoot no more/hasheater
User ID: 1385015
United Kingdom
05/15/2011 07:09 PM
Report Abusive Post
Report Copyright Violation
Re: SPECULATION: Could temporally transient and spatially isolated magnetic field fluctuations be causing the transformer failures?
OMG so rare for GLP, a civil disagreement!.......thanks guys!





GLP