Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
My garage has very little electricity. Less than 4 lights, only one wall plus ceiling has outlets. I need to add breaker box for upgrades including 220 for air compressor.

I bought a small 110 compressor and it pops basement breaker when it comes on if any lights are on too.

I'm worried about and have no knowledge fishing wires from basement to garage. Any experienced answers would be great.
Will we even know we were alive when we're dead? Me

Kingdoms were run by kings
Empires were run by Emperors
Countries are run by.....
Dumps were almost fixed by Trump
Anonymous Coward
User ID: 70491268
United States
02/24/2016 11:44 AM
Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
First off, you should see what amp panel you have. Is it a 100 amp or 200 amp box? Usually looking at the main breaker will tell you this.
ChvyV8Bldr  (OP)

User ID: 21517811
United States
02/24/2016 11:47 AM

Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
First off, you should see what amp panel you have. Is it a 100 amp or 200 amp box? Usually looking at the main breaker will tell you this.
 Quoting: Anonymous Coward 70491268


My house is 150 amp
Will we even know we were alive when we're dead? Me

Kingdoms were run by kings
Empires were run by Emperors
Countries are run by.....
Dumps were almost fixed by Trump
ChvyV8Bldr  (OP)

User ID: 21517811
United States
02/24/2016 11:50 AM

Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
My garage has very little electricity. Less than 4 lights, only one wall plus ceiling has outlets. I need to add breaker box for upgrades including 220 for air compressor.

I bought a small 110 compressor and it pops basement breaker when it comes on if any lights are on too.

I'm worried about and have no knowledge fishing wires from basement to garage. Any experienced answers would be great.
 Quoting: ChvyV8Bldr


Hire a professional tard.
 Quoting: Anonymous Coward 69210878


My last garage had 200 amp service and I wired the whole garage. I know electricity, just never ran from one building to another.
Will we even know we were alive when we're dead? Me

Kingdoms were run by kings
Empires were run by Emperors
Countries are run by.....
Dumps were almost fixed by Trump
Anonymous Coward
User ID: 4929481
United States
02/24/2016 11:50 AM
Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
My garage has very little electricity. Less than 4 lights, only one wall plus ceiling has outlets. I need to add breaker box for upgrades including 220 for air compressor.

I bought a small 110 compressor and it pops basement breaker when it comes on if any lights are on too.

I'm worried about and have no knowledge fishing wires from basement to garage. Any experienced answers would be great.
 Quoting: ChvyV8Bldr


Hire a professional tard.
 Quoting: Anonymous Coward 69210878


hesright

Based on your posts, you really are not at all bright, OP.

Best leave these sorts of jobs to the pros, so you don't end up burning down your house, or worse, your neighborhood.
 Quoting: Anonymous Coward 52765227


You obviously don't know me.
 Quoting: ChvyV8Bldr



Regaurdless, they are right. Adding a 220 circus is not really something you should do yourself.


As far fishing down your romex cable you are going to have to cut the drywall at the floor so you can make a penny ration through your base board.
Anonymous Coward
User ID: 70491268
United States
02/24/2016 11:52 AM
Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
First off, you should see what amp panel you have. Is it a 100 amp or 200 amp box? Usually looking at the main breaker will tell you this.
 Quoting: Anonymous Coward 70491268


My house is 150 amp
 Quoting: ChvyV8Bldr


Well, you need to figure up the amperage of all the major stuff in your house and see how much you have left over to get to 150 amps. This will be what you can safely run to your garage without tripping that 150 amp breaker all the time.

Otherwise you will need a separate service run to your garage.

Of course you could time your garage activities when your not cooking, running the clothes dier, ect. But you need to know how close you are to maxing out your box amperage as it stands. If you dont have 30 or so amps left over, I wouldnt try coming off your regular house panel. Are you planning on using a welder?
ChvyV8Bldr  (OP)

User ID: 21517811
United States
02/24/2016 11:57 AM

Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
First off, you should see what amp panel you have. Is it a 100 amp or 200 amp box? Usually looking at the main breaker will tell you this.
 Quoting: Anonymous Coward 70491268


My house is 150 amp
 Quoting: ChvyV8Bldr


Well, you need to figure up the amperage of all the major stuff in your house and see how much you have left over to get to 150 amps. This will be what you can safely run to your garage without tripping that 150 amp breaker all the time.

Otherwise you will need a separate service run to your garage.

Of course you could time your garage activities when your not cooking, running the clothes dier, ect. But you need to know how close you are to maxing out your box amperage as it stands. If you dont have 30 or so amps left over, I wouldnt try coming off your regular house panel. Are you planning on using a welder?
 Quoting: Anonymous Coward 70491268


Yes I know this. I am running new service from my existing panel in my basement thru the conduit to the garage where I'm installing a new panel.

No welder. I need it for an old air compressor. I won't need over 100 amps in the garage.
Will we even know we were alive when we're dead? Me

Kingdoms were run by kings
Empires were run by Emperors
Countries are run by.....
Dumps were almost fixed by Trump
ChvyV8Bldr  (OP)

User ID: 21517811
United States
02/24/2016 12:00 PM

Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
First off, you should see what amp panel you have. Is it a 100 amp or 200 amp box? Usually looking at the main breaker will tell you this.
 Quoting: Anonymous Coward 70491268


My house is 150 amp
 Quoting: ChvyV8Bldr


Well, you need to figure up the amperage of all the major stuff in your house and see how much you have left over to get to 150 amps. This will be what you can safely run to your garage without tripping that 150 amp breaker all the time.

Otherwise you will need a separate service run to your garage.

Of course you could time your garage activities when your not cooking, running the clothes dier, ect. But you need to know how close you are to maxing out your box amperage as it stands. If you dont have 30 or so amps left over, I wouldnt try coming off your regular house panel. Are you planning on using a welder?
 Quoting: Anonymous Coward 70491268


Yes I know this. I am running new service from my existing panel in my basement thru the conduit to the garage where I'm installing a new panel.

No welder. I need it for an old air compressor. I won't need over 100 amps in the garage.
 Quoting: ChvyV8Bldr

Don't do laundry at this house, and cooking with gas.
Will we even know we were alive when we're dead? Me

Kingdoms were run by kings
Empires were run by Emperors
Countries are run by.....
Dumps were almost fixed by Trump
Anonymous Coward
User ID: 10630957
United States
02/24/2016 12:00 PM
Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
really need to pay someone.

Here goes.

4 lights throwing a breaker???? are you running 1000watt HPS grow lights or 4 CFL shop lights.... big difference like 3600 watts difference.

I never pull more than 1250 watts on a 15 amp or 2000 on a 20amp.

but I would pull a 220 line from your box (it will have a 2 spot 50amp I believe) run it in Grey plastic 1 inch (electric grade) pipe under the ground. (I would go at least 1 foot in the ground.

Inside the "Garage" I would have another smaller fuse box and split it into double pole 20 amp breakers.

Then you can use on for the lights/others and another for your power tools.

BUT BUT BUT double check because the way I explain it and the way I see it in my mind might be different in your head.

after you do it pay an electrician friend $100 to make sure you hook it up right.
Anonymous Coward
User ID: 63773885
United States
02/24/2016 12:02 PM
Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
I work for an electrical distribution company. Don't try this yourself.

I would separate to two circuits (house and garage) and add a 2nd meter to the garage. The monthly cost is nominal and if you're tripping breakers you can't handle the extra load (current, amps) you're adding to the garage

If you plan on doing business out of the garage you then have a tax break for the work you're doing and the usages on the meter
Anonymous Coward
User ID: 71109760
United States
02/24/2016 12:04 PM
Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
My garage has very little electricity. Less than 4 lights, only one wall plus ceiling has outlets. I need to add breaker box for upgrades including 220 for air compressor.

I bought a small 110 compressor and it pops basement breaker when it comes on if any lights are on too.

I'm worried about and have no knowledge fishing wires from basement to garage. Any experienced answers would be great.
 Quoting: ChvyV8Bldr


Hire a professional tard.
 Quoting: Anonymous Coward 69210878


hesright

Based on your posts, you really are not at all bright, OP.

Best leave these sorts of jobs to the pros, so you don't end up burning down your house, or worse, your neighborhood.
 Quoting: Anonymous Coward 52765227


Tho the language is harsh, the message is right.....I know how to do electrical work, BUT I hire a pro to do it.....why? cuz should there be a fire or a mishap, the insurance company will not pay.....Plus the work you are need done requires a permit to be pulled....
Anonymous Coward
User ID: 63773885
United States
02/24/2016 12:04 PM
Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
Look up Ohms law if you have questions about load.

E x I = P

Volts x amps x power factor = watts
ChvyV8Bldr  (OP)

User ID: 21517811
United States
02/24/2016 12:04 PM

Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
I work for an electrical distribution company. Don't try this yourself.

I would separate to two circuits (house and garage) and add a 2nd meter to the garage. The monthly cost is nominal and if you're tripping breakers you can't handle the extra load (current, amps) you're adding to the garage

If you plan on doing business out of the garage you then have a tax break for the work you're doing and the usages on the meter
 Quoting: Anonymous Coward 63773885


I've considered this and chose not to.
Will we even know we were alive when we're dead? Me

Kingdoms were run by kings
Empires were run by Emperors
Countries are run by.....
Dumps were almost fixed by Trump
Anonymous Coward
User ID: 70491268
United States
02/24/2016 12:08 PM
Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
...


My house is 150 amp
 Quoting: ChvyV8Bldr


Well, you need to figure up the amperage of all the major stuff in your house and see how much you have left over to get to 150 amps. This will be what you can safely run to your garage without tripping that 150 amp breaker all the time.

Otherwise you will need a separate service run to your garage.

Of course you could time your garage activities when your not cooking, running the clothes dier, ect. But you need to know how close you are to maxing out your box amperage as it stands. If you dont have 30 or so amps left over, I wouldnt try coming off your regular house panel. Are you planning on using a welder?
 Quoting: Anonymous Coward 70491268


Yes I know this. I am running new service from my existing panel in my basement thru the conduit to the garage where I'm installing a new panel.

No welder. I need it for an old air compressor. I won't need over 100 amps in the garage.
 Quoting: ChvyV8Bldr

Don't do laundry at this house, and cooking with gas.
 Quoting: ChvyV8Bldr


Well, if you have enough amperage left over, you can get a breaker with that rating and run the garage off that. Next step is to figure what size wire you need. You wont know that till you figure out how much amperage you can safely pull from your box.

Of course the smaller the wire, the easier it will be to get through the conduit, if it will go at all.
ChvyV8Bldr  (OP)

User ID: 21517811
United States
02/24/2016 12:09 PM

Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
really need to pay someone.

Here goes.

4 lights throwing a breaker???? are you running 1000watt HPS grow lights or 4 CFL shop lights.... big difference like 3600 watts difference.

I never pull more than 1250 watts on a 15 amp or 2000 on a 20amp.

but I would pull a 220 line from your box (it will have a 2 spot 50amp I believe) run it in Grey plastic 1 inch (electric grade) pipe under the ground. (I would go at least 1 foot in the ground.

Inside the "Garage" I would have another smaller fuse box and split it into double pole 20 amp breakers.

Then you can use on for the lights/others and another for your power tools.

BUT BUT BUT double check because the way I explain it and the way I see it in my mind might be different in your head.

after you do it pay an electrician friend $100 to make sure you hook it up right.
 Quoting: Anonymous Coward 10630957


No, the garage hasn't been updated probably since being built. When my small air compressor comes on the breaker trips. Plus I need 220. I know how to work with electricity.

Back to my original question.

Has any body ran bigger ga. Wire from their home box to their garage using the existing conduit that's already under ground?

Last Edited by TwentyTwenty on 02/24/2016 12:10 PM
Will we even know we were alive when we're dead? Me

Kingdoms were run by kings
Empires were run by Emperors
Countries are run by.....
Dumps were almost fixed by Trump
Anonymous Coward
User ID: 14572610
Canada
02/24/2016 12:09 PM
Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
How many amps is your main service?

If it's 100 of less amps, likely won't have enough to add a pony panel in your garage..

If you have a 200 amp service it is pretty simple.

Buy a 60 amp pony panel, add a 60 amp breaker to your main, run wire from main panel to where your pony panel is or conduit, then branch circuits from your new pony panel.
ChvyV8Bldr  (OP)

User ID: 21517811
United States
02/24/2016 12:11 PM

Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
How many amps is your main service?

If it's 100 of less amps, likely won't have enough to add a pony panel in your garage..

If you have a 200 amp service it is pretty simple.

Buy a 60 amp pony panel, add a 60 amp breaker to your main, run wire from main panel to where your pony panel is or conduit, then branch circuits from your new pony panel.
 Quoting: Anonymous Coward 14572610


Again, it's 150
Will we even know we were alive when we're dead? Me

Kingdoms were run by kings
Empires were run by Emperors
Countries are run by.....
Dumps were almost fixed by Trump
Anonymous Coward
User ID: 70491268
United States
02/24/2016 12:12 PM
Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
really need to pay someone.

Here goes.

4 lights throwing a breaker???? are you running 1000watt HPS grow lights or 4 CFL shop lights.... big difference like 3600 watts difference.

I never pull more than 1250 watts on a 15 amp or 2000 on a 20amp.

but I would pull a 220 line from your box (it will have a 2 spot 50amp I believe) run it in Grey plastic 1 inch (electric grade) pipe under the ground. (I would go at least 1 foot in the ground.

Inside the "Garage" I would have another smaller fuse box and split it into double pole 20 amp breakers.

Then you can use on for the lights/others and another for your power tools.

BUT BUT BUT double check because the way I explain it and the way I see it in my mind might be different in your head.

after you do it pay an electrician friend $100 to make sure you hook it up right.
 Quoting: Anonymous Coward 10630957


No, the garage hasn't been updated probably since being built. When my small air compressor comes on the breaker trips. Plus I need 220. I know how to work with electricity.

Back to my original question.

Has any body ran bigger ga. Wire from their home box to their garage using the existing conduit that's already under ground?
 Quoting: ChvyV8Bldr


Yes. Lots of dish soap helps.
ChvyV8Bldr  (OP)

User ID: 21517811
United States
02/24/2016 12:13 PM

Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
How many amps is your main service?

If it's 100 of less amps, likely won't have enough to add a pony panel in your garage..

If you have a 200 amp service it is pretty simple.

Buy a 60 amp pony panel, add a 60 amp breaker to your main, run wire from main panel to where your pony panel is or conduit, then branch circuits from your new pony panel.
 Quoting: Anonymous Coward 14572610


Again, it's 150
 Quoting: ChvyV8Bldr
And it’s already run underground.
Will we even know we were alive when we're dead? Me

Kingdoms were run by kings
Empires were run by Emperors
Countries are run by.....
Dumps were almost fixed by Trump
Anonymous Coward
User ID: 41915071
United States
02/24/2016 12:14 PM
Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
Use this calculator to calculate the gauge wire you need to feed the subpanel in the garage.

Where is the breaker that is popping?

If the voltage drop to the compressor is signifficant, this will effect the start current of the motor a lot ...... i.e. pop your breaker.

Sounds like you need to look at the wire size feeding your subpanel.

[link to www.paigewire.com]
ChvyV8Bldr  (OP)

User ID: 21517811
United States
02/24/2016 12:14 PM

Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
really need to pay someone.

Here goes.

4 lights throwing a breaker???? are you running 1000watt HPS grow lights or 4 CFL shop lights.... big difference like 3600 watts difference.

I never pull more than 1250 watts on a 15 amp or 2000 on a 20amp.

but I would pull a 220 line from your box (it will have a 2 spot 50amp I believe) run it in Grey plastic 1 inch (electric grade) pipe under the ground. (I would go at least 1 foot in the ground.

Inside the "Garage" I would have another smaller fuse box and split it into double pole 20 amp breakers.

Then you can use on for the lights/others and another for your power tools.

BUT BUT BUT double check because the way I explain it and the way I see it in my mind might be different in your head.

after you do it pay an electrician friend $100 to make sure you hook it up right.
 Quoting: Anonymous Coward 10630957


No, the garage hasn't been updated probably since being built. When my small air compressor comes on the breaker trips. Plus I need 220. I know how to work with electricity.

Back to my original question.

Has any body ran bigger ga. Wire from their home box to their garage using the existing conduit that's already under ground?
 Quoting: ChvyV8Bldr


Yes. Lots of dish soap helps.
 Quoting: Anonymous Coward 70491268


LoL TBH, that's the best answer yet.
Will we even know we were alive when we're dead? Me

Kingdoms were run by kings
Empires were run by Emperors
Countries are run by.....
Dumps were almost fixed by Trump
Anonymous Coward
User ID: 29285147
United States
02/24/2016 12:15 PM
Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
If your were stumped by tack strips OP, you definitely don't want to mess with 220v. At least get a pro to assist you.


------
Anonymous Coward
User ID: 70491268
United States
02/24/2016 12:16 PM
Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
I would use the existing wire as a pull wire, then connect to the new cable by twisting the wires together where they wouldnt come apart. Then use tape to make it a smooth joint. Have someone pulling on one end and someone pushing on the other while adding the dish soap as it goes into the conduit.
Anonymous Coward
User ID: 41915071
United States
02/24/2016 12:18 PM
Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
I would use the existing wire as a pull wire, then connect to the new cable by twisting the wires together where they wouldnt come apart. Then use tape to make it a smooth joint. Have someone pulling on one end and someone pushing on the other while adding the dish soap as it goes into the conduit.
 Quoting: Anonymous Coward 70491268


Go to Home Depot and get wire lube. Works awesome, as dish soap will dry and coagulate quickly
[link to www.homedepot.com]
ChvyV8Bldr  (OP)

User ID: 21517811
United States
02/24/2016 12:19 PM

Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
If your were stumped by tack strips OP, you definitely don't want to mess with 220v. At least get a pro to assist you.


------
 Quoting: halman


Of course. My electrician buddy of mine are gonna get drunk and do it this weekend. Carpentry is not electrical work.
Will we even know we were alive when we're dead? Me

Kingdoms were run by kings
Empires were run by Emperors
Countries are run by.....
Dumps were almost fixed by Trump
trueforger

User ID: 70996005
United States
02/24/2016 12:19 PM
Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
really need to pay someone.

Here goes.

4 lights throwing a breaker???? are you running 1000watt HPS grow lights or 4 CFL shop lights.... big difference like 3600 watts difference.

I never pull more than 1250 watts on a 15 amp or 2000 on a 20amp.

but I would pull a 220 line from your box (it will have a 2 spot 50amp I believe) run it in Grey plastic 1 inch (electric grade) pipe under the ground. (I would go at least 1 foot in the ground.

Inside the "Garage" I would have another smaller fuse box and split it into double pole 20 amp breakers.

Then you can use on for the lights/others and another for your power tools.

BUT BUT BUT double check because the way I explain it and the way I see it in my mind might be different in your head.

after you do it pay an electrician friend $100 to make sure you hook it up right.
 Quoting: Anonymous Coward 10630957


No, the garage hasn't been updated probably since being built. When my small air compressor comes on the breaker trips. Plus I need 220. I know how to work with electricity.

Back to my original question.

Has any body ran bigger ga. Wire from their home box to their garage using the existing conduit that's already under ground?
 Quoting: ChvyV8Bldr


Yes. Lots of dish soap helps.
 Quoting: Anonymous Coward 70491268

Pulling wire in conduit is less easy than it seems like it ought to be. Bends and leaving the old wire makes it worse. Definitely use some wire puller lubricant, it's cheaper than dish soap. Using a shop vac to pull string through the run is way easier than a metal fish tape. Remember to never coil wires run underground in conduit, you'll be making an electromagnet that wastes electrical power, causes ground voltage problems, disturbs animals and electronics.

How far?
Blacksmith King of Trades
I make your tool DEPLORABLE
MAKING AMERICA GREAT AGAIN VULGARIAN
LOVE TRUMP'S DEPLORABLE HATE
Wisconsin=Deplorable Honey Badger State
"We have to re-jigger it" VULGARIAN
"Tough times don't last, Tough People do." DEPLORABLE
Anonymous Coward
User ID: 69797435
United States
02/24/2016 12:21 PM
Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
The lazy man's approach would be to get you some buriable 6/3 or 6/4 UV cable and avoid pulling through conduit altogether.
ChvyV8Bldr  (OP)

User ID: 21517811
United States
02/24/2016 12:21 PM

Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
I would use the existing wire as a pull wire, then connect to the new cable by twisting the wires together where they wouldnt come apart. Then use tape to make it a smooth joint. Have someone pulling on one end and someone pushing on the other while adding the dish soap as it goes into the conduit.
 Quoting: Anonymous Coward 70491268


Go to Home Depot and get wire lube. Works awesome, as dish soap will dry and coagulate quickly
[link to www.homedepot.com]
 Quoting: Anonymous Coward 41915071


Thank you. Fuckin A. Thank you. This is the type of answer I was looking for.
Will we even know we were alive when we're dead? Me

Kingdoms were run by kings
Empires were run by Emperors
Countries are run by.....
Dumps were almost fixed by Trump
ChvyV8Bldr  (OP)

User ID: 21517811
United States
02/24/2016 12:23 PM

Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
really need to pay someone.

Here goes.

4 lights throwing a breaker???? are you running 1000watt HPS grow lights or 4 CFL shop lights.... big difference like 3600 watts difference.

I never pull more than 1250 watts on a 15 amp or 2000 on a 20amp.

but I would pull a 220 line from your box (it will have a 2 spot 50amp I believe) run it in Grey plastic 1 inch (electric grade) pipe under the ground. (I would go at least 1 foot in the ground.

Inside the "Garage" I would have another smaller fuse box and split it into double pole 20 amp breakers.

Then you can use on for the lights/others and another for your power tools.

BUT BUT BUT double check because the way I explain it and the way I see it in my mind might be different in your head.

after you do it pay an electrician friend $100 to make sure you hook it up right.
 Quoting: Anonymous Coward 10630957


No, the garage hasn't been updated probably since being built. When my small air compressor comes on the breaker trips. Plus I need 220. I know how to work with electricity.

Back to my original question.

Has any body ran bigger ga. Wire from their home box to their garage using the existing conduit that's already under ground?
 Quoting: ChvyV8Bldr


Yes. Lots of dish soap helps.
 Quoting: Anonymous Coward 70491268

Pulling wire in conduit is less easy than it seems like it ought to be. Bends and leaving the old wire makes it worse. Definitely use some wire puller lubricant, it's cheaper than dish soap. Using a shop vac to pull string through the run is way easier than a metal fish tape. Remember to never coil wires run underground in conduit, you'll be making an electromagnet that wastes electrical power, causes ground voltage problems, disturbs animals and electronics.

How far?
 Quoting: trueforger


From my basement to the garage maybe 20 feet.
Will we even know we were alive when we're dead? Me

Kingdoms were run by kings
Empires were run by Emperors
Countries are run by.....
Dumps were almost fixed by Trump
ChvyV8Bldr  (OP)

User ID: 21517811
United States
02/24/2016 12:25 PM

Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
...


No, the garage hasn't been updated probably since being built. When my small air compressor comes on the breaker trips. Plus I need 220. I know how to work with electricity.

Back to my original question.

Has any body ran bigger ga. Wire from their home box to their garage using the existing conduit that's already under ground?
 Quoting: ChvyV8Bldr


Yes. Lots of dish soap helps.
 Quoting: Anonymous Coward 70491268

Pulling wire in conduit is less easy than it seems like it ought to be. Bends and leaving the old wire makes it worse. Definitely use some wire puller lubricant, it's cheaper than dish soap. Using a shop vac to pull string through the run is way easier than a metal fish tape. Remember to never coil wires run underground in conduit, you'll be making an electromagnet that wastes electrical power, causes ground voltage problems, disturbs animals and electronics.

How far?
 Quoting: trueforger


From my basement to the garage maybe 20 feet.
 Quoting: ChvyV8Bldr


I could solder the updated wire to the old wire for a more secure pull, no?
Will we even know we were alive when we're dead? Me

Kingdoms were run by kings
Empires were run by Emperors
Countries are run by.....
Dumps were almost fixed by Trump
Anonymous Coward
User ID: 63773885
United States
02/24/2016 12:25 PM
Report Abusive Post
Report Copyright Violation
Re: Electricians help. Has anybody pulled wire from house to detached garage to add breaker box and 220?
really need to pay someone.

Here goes.

4 lights throwing a breaker???? are you running 1000watt HPS grow lights or 4 CFL shop lights.... big difference like 3600 watts difference.

I never pull more than 1250 watts on a 15 amp or 2000 on a 20amp.

but I would pull a 220 line from your box (it will have a 2 spot 50amp I believe) run it in Grey plastic 1 inch (electric grade) pipe under the ground. (I would go at least 1 foot in the ground.

Inside the "Garage" I would have another smaller fuse box and split it into double pole 20 amp breakers.

Then you can use on for the lights/others and another for your power tools.

BUT BUT BUT double check because the way I explain it and the way I see it in my mind might be different in your head.

after you do it pay an electrician friend $100 to make sure you hook it up right.
 Quoting: Anonymous Coward 10630957


No, the garage hasn't been updated probably since being built. When my small air compressor comes on the breaker trips. Plus I need 220. I know how to work with electricity.

Back to my original question.

Has any body ran bigger ga. Wire from their home box to their garage using the existing conduit that's already under ground?
 Quoting: ChvyV8Bldr


There are codes that limit the size and number of conductors that can be ran thru conduit.

If your conduit is big enough to handle larger conductor and it will pass inspection then you attach the new conductor to the end of the old ,usually a pulling sock and electrical tape and pull





GLP